Yes it was the cladding but expert reports for the public inquiry into the Grenfell Tower fire find multiple fire safety failures in the building and its refurbishment and management and in the wider regulatory system and construction industry.
The first thing that leaps out of the report by fire engineer Dr Barbara Lane is a timeline that shows that the conditions for ‘Stay Put’ advice to residents had ‘substantially failed’ by 01:26 on the morning of the fire.
This was within half an hour of the fire breaking out in Flat 16 and the London Fire Brigade did not abandon Stay Put until 02:47.
Those conclusions have already made some of the headlines but Dr Lane makes clear that there is a deeper context for them.
The way that high-rise buildings are designed and the way that fires in them are fought in them rely on the fact that multi-storey external envelope fires are not meant to happen.
So the fire at Grenfell rendered invalid all of the basic assumptions about fighting fires from the inside and telling residents of other flats to stay inside them because they will be protected by compartmentation.
That meant there had to be an improvised approach to fighting the fire from the outside on the night but most of the building was always going to out of reach even for aerial appliances – the whole reason why the risk of external fires should be designed out in the first place.
Fire safety relies on ‘defence in depth’ or multiple levels of safety, meaning not just compartmentation but a whole range of other levels such as provision of firefighting equipment, fire doors, smoke control, ventilation of the staircase, fire alarms and active and passive fire protection systems. But once the fire spread they began to fail one by one.
As Dr Lane puts it:
‘The building envelope created an intolerable risk on the night of the fire, resulting in extreme harm. It did not adequately resist the spread of fire over the walls having regard to the height and use of the building. The active and passive fire protection measures within the Tower were then required to mitigate an extraordinary event, and as a result, the consequences were catastrophic.’
She concludes based on test evidence supplied to the inquiry that the construction materials forming the rainscreen cladding system ‘did not comply with the recommended fire performance set out in the statutory guidance of [Approved Document] B 2013 for a building of that height’.
But the problems went beyond just the cladding, with ‘multiple catastrophic fire-spread routes’ created by the construction form and detailing and the arrangement of materials used around the old and new windows increasing the likelihood that fire would spread from a flat to the cavities in the cladding system.
Attempts had been made to subdivide the cavities but both the horizontal and vertical fire stopping were installed incorrectly, and ‘no evidence has been provided that they were ever tested for performance in an ACP based rainscreen cladding system of the type installed at Grenfell Tower’.
The windows did not have fire resisting cavity barriers and ‘these unprotected openings themselves were surrounded by combustible material’, meaning that there was ‘a disproportionately high probability of a fire starting near a window spreading to the cladding.
The arrangement and type of construction materials in the cladding system then stretched the rest of the fire safety system to breaking point, with multiple internal fires, large amounts of smoke, an early need for external firefighting and a need to change the evacuation strategy.
She finds that the cladding system was ‘therefore non-compliant with the functional requirement of the Building Regulations’ but
All of that had severe knock-on effects for the firefighting operation with the Fire Brigade never told that there was a combustible cladding system.
In one of the most damning sections of the entire report she says:
‘I have found no evidence yet that any member of the design team or the construction team ascertained the fire performance of the rainscreen cladding system materials, nor understood how the assembly performed in fire. I have found no evidence that Building Control were either informed or understood how the assembly would perform in a fire. Further I have found no evidence that the TMO risk assessment recorded the fire performance of the rainscreen cladding system, nor have I found evidence that the LFB risk assessment recorded the fire performance of the rainscreen cladding system.’
On Stay Put, Dr Lane says she is particularly concerned about the delay between 02:06, when a major incident was declared, and 02:47 when the advice was changed.
However, she points out that there is no requirement in the UK for automatic detection and alarm systems in high-rise buildings and so no way to raise an all-out alarm in Grenfell Tower or to communicate with vulnerable residents.
As the report makes clear, Grenfell went through an extensive refurbishment between 2012 and 2016, including not just the cladding but also full internal refurbishment of the first three storeys, work on the building services on every floor and in every flat, replacement of all the fire doors and gas supply works.
The problems with the fire doors are now well known. The report says that the installed doors had different metal fittings and intumescent seals, which could have affected their performance and some were glazed and could have failed prematurely
Dr Lane concludes that ‘all the flat entrance doors (from Level 4-23) were non-compliant with the fire test evidence relied on at the time of the installation’ and that this non-compliance ‘would have contributed to the failure to prevent the spread of fire and hot smoke from the fire to the lobby’.
There were further failures of the ventilation system that was meant to extract smoke from the lobbies and of the fire lift, with the Fire Brigade unable to take control.
Grenfell also had a dry fire main rather than a wet one, making it non-compliant with design guidance at the time of the original construction and with current standards.
A wet main would have enabled a faster response to the original fire and enabled greater water pressure but even they are not designed for the multiple hoses needed.
That non-compliance contributed to a failure to prevent the spread of fire and hot smoke from the flat to the lobby.
Overall, Dr Lane finds that:
‘The number of non-compliances signify a culture of non-compliance at Grenfell Tower. I am particularly concerned about the maintenance regime of the active and passive fire protection measures. I note that multiple automatic systems such as the control of the fire lift and the smoke ventilation system, appear not to have operated as required.’
That and other issues such as the gas installation will be covered in Phase 2 of her report.
(...)
[Birch then summarizes a number of Lane's conclusions including] :
Communications with residents – even if the advice at Grenfell had been changed more quickly from ‘Stay Put’ to ‘All Out’ it’s not clear how the message could have been communicated to residents. Dr Lane points out change to Stay Put is not easy in the UK because there is no statutory requirement for automatic detection and alarm systems to warn residents of high-rise buildings.