The level of known facts has increased as this thread has gone on.
The following are some of the known relevant aspects of the situation
- The insulation used was certified for use in above 18m buildings (BS 8414-2:2005) only if a specified installation method is used with regular fire stops and with a certain type of intrinsically rigid and non-combustible cladding.
The cladding in this installation was not the cladding used to gain the certification, and had an HDPE core to provide rigidity that would melt at around 115-135 degC.
Fire stops appear to have been installed (judging from photos of before and after), but the building looks incredibly difficult for this to have been done in a way that created fully sealed fire stops throughout.
- The cladding was using Renubond PE. The manufacturer claims both this and the Renubond FR cladding meeting class O under BS 476 UK fire regs, which would mean that either would seem to meet the requirements of Diagram D (page 95) of ADB2 for external finishes of walls. However it gives no further details, and doesn't included the PE version at all in the more detailed fire safety document for high rise buildings. It also has a diagram showing the PE should only be used for cladding on buildings under 10m on page 1 of that document.
- The building was recently refitted with combi boilers in each flat, each needing to be vented through an external wall.
This provides a potential route for fire to get out to the cladding, a route for smoke and fire to enter the building from the cladding, and a potential additional fuel source for any cladding fire if any boilers were damaged.
From this it seems that the exact combination of cladding and insulation used here were not certified for this use, unless they'd been specifically tested by the installation company or either supply company for this installation method and that test result isn't available online.
It's also possible to see why the specifiers would have missed this, as you need to really dig into the literature to sus this out, the datasheets do not make this clear and the cladding by itself actually would have been allowed as it meets the required BS 476 standard, it's only the combination that probably isn't certified.
There is a serious problem though with the all the standards involved here. OU took the piss out of my burner test, but essentially that is the main BS test that's used other than it also being electrically heated and under STC.
This
article explains the different fire regulations standards, and why the PE variant of the cladding might pass the UK standard but not the German standard (flame applied to the side of the cladding vs the base of it).
There's also the issue that with the external insulation the class 0 requirement is lower than for other elements, it's allowed to flame for up to 10 seconds, and give a 25 deg temp rise, vs the standard requirement of no flame and a 20 degree maximum rise. So even a Class 0 pass isn't the same standard for all products. ie for insulated cladding it's allowed to catch fire and flame, so it will add to any fire that is already burning but that's fine as long it goes out within 10 seconds of the other source of the fire going out.
What was and is really needed is a requirement for all elements of the cladding and insulation to be non-combustible, to not flame at all, rather than allowing all these complex varieties of it being allowed to burn a bit in certain situations but then being controlled by xyz additional measures and installation methods.